Having been bit by it, I know it's there. This deals with a solidly grounded 480V generator (2MW in the case at hand) to be paralleled with a utility service. Draw the SLG fault sequence diagram (physically or mentally). Now assign the following values: Utility Z1, Z2, Z0 - medium with Z0 a medium high (grounded-wye / grounded-wye service transformer) or medium low (delta / grounded-wye service transformer). Generator Z1, Z2 - high, Z0 - low (or even really low).
Utility alone fault current flows through three medium (+/-)impedances and produces a medium current. Generator alone the fault current flows through two high impedances and one low impedance and produces a low fault current. So far, so good. Now, put the two in parallel and what you have is Z1 and Z2 are the parallel combination of medium and high, or something less than medium, but Z0 is now the parallel combination of medium and low, or something even lower than low, so the fault current is quite high.
Thinking about the diagrams now, I guess the 3-phase would be the sum of the two, but the SLG is most definitely not. When you have a utility SLG value of about 30kA and a generator SLG in the high 20kA range and you put them in parallel and the analysis software spits out upward of 80kA fault current (I don't have the exact numbers at hand from that project but the general order of magnitude is right) it really grabs your attention. That was the only time I found the need to do a hand calc to verify what SKM was telling me, and by gum they were right and my 65kA gear was in trouble.
There are advantages to working with the utility on projects that they want to make happen at a reasonable cost (read utility funded) - I got out of that bind by getting them to provide real transformer impedances and real system impedances ahead of the service and that knocked my fault currents way down and 65kA was great plenty.
Gotta watch those generator Z0 values for solidly grounded machines; Z0 is basically just the DC resistance of the windings and that is very low.