I don't trust the numbers shown on that print out very much. If there were to be a difference between the two hold downs, I would expect the outer hold down to take the greater load. Sigma = Mc/I after all....
It's always a little problematic putting in two perfectly rigid supports so close to each other. Therefore, you might either do a hand calc (like AELLC suggests), or replace the perfectly rigid reaction with a more flexible spring support.
The real behavior of a shear wall is actually a lot different than that model. You have continuous shear resistance along the length of the wall. You have continuous compressive vertical resistance along the wall. Heck, you probably have something close to contiunous tensile resistance as well. The NDS stiffness and deflection equations assume this type of continous resistance as well....we just don't rely on it for design purposes. Instead, we create a pretend force couple in the chords to resist the total moment. At least that's the current "standard of care" in the industry. If you do something else (however rational) then you probably want it to be more conservative than what the hand calc method would give.