Looking for a little clarification on ASCE 7-05 Section 6.4.2.1.1 Minimum Pressures. In that section it says that all pressures in Zones A, B, C, and D should be +10psf while Zones E, F, G, and H should all be 0psf. This is where my question comes in. If my Zone B pressure calcs out to be 5 psf should I then use 10 psf as a minimum design for overturning of a shear wall and set uplift pressures equal to zero? (Case 2 in attachment) It seems highly unconservative to neglect uplift forces for overturning of shear walls. Or is the correct procedure to use the calculated value of 5 psf + Zone C + Net Uplift for overturning and the minimum 10 psf + Zone C when determining shear only forces. I have attached an arbitrary interior shear wall for review.
Thanks much!
Looking for a little clarification on ASCE 7-05 Section 6.4.2.1.1 Minimum Pressures. In that section it says that all pressures in Zones A, B, C, and D should be +10psf while Zones E, F, G, and H should all be 0psf. This is where my question comes in. If my Zone B pressure calcs out to be 5 psf should I then use 10 psf as a minimum design for overturning of a shear wall and set uplift pressures equal to zero? (Case 2 in attachment) It seems highly unconservative to neglect uplift forces for overturning of shear walls. Or is the correct procedure to use the calculated value of 5 psf + Zone C + Net Uplift for overturning and the minimum 10 psf + Zone C when determining shear only forces. I have attached an arbitrary interior shear wall for review.
Thanks much!