MegaStructures
Structural
- Sep 26, 2019
- 376
ACI code 318-14 section 8.4.4.2 gives provisions to transfer slab moments to columns through flexural action and eccentric shear as can be seen in the first two images below. My question applies to the shear requirement only. The provisions are clear for determining if shear reinforcement is needed. However, once it is determined that reinforcement is needed it is not clear whether the eccentric shear should be considered on the second critical section a distance d/2 away from the last reinforcement. Is eccentric shear only considered at the first critical section? Or should it be considered when finding the point that shear reinforcement can be stopped? Image of second critical section is shown in the third picture.


