Hi,
AISC Design guide 1 provides different capacities for shear lug bearing against concrete (0.8fc) and column bearing against concrete (0.55fc). Why is there a difference? I know 0.8fc comes from ACI - 349. Is the difference because of different experimental setups?
Also, what value to use while checking shear lug bearing? I am tending to use 0.8fc as the design guide clearly states bearing capacity for shear lug as 0.8fc. Any opinions?
Thanks