Kstructuralguy
Structural
- Mar 6, 2018
- 6
I need to check a hollowcore plank's capacity to resist shear breakout force applied by embedded anchors. The anchors are post installed, and embedded though the entire plank (top flange through to the bottom flange and through a hollow core, not into a web). The shear force is parallel to the span of the hollowcore plank.
To check the plank's capacity, I used ACE318-11 Appendix D ( Section 17.5 in ACI318-14) as advised in the PCI Handbook. Initially, I only considered the breakout area of the flanges for simplicity. The cores will be grouted at the anchors but since the plank has already been cast, the only thing holding the grouted core in place if there is a failure is friction so I cannot account for that to add to the breakout capacity. This calculation does not produce the required strength, so I included the webs of the plank within the breakout area.
This is where things become unclear. The basic concrete breakout strength in shear of a single anchor, Vb, (section D6.2.2 in ACI318-11) needs the required load bearing length of the anchor, le. So question #1: If each flange is 1" thick, the load bearing length, le, is 2" regardless of if the cell is grouted correct? Since the grouted section is not load bearing.
The bigger point of uncertainty is the "modification factor for anchors located in a concrete member where ha < 1.5*ca1" (section D.6.2.8 in ACI318-11). If ha is taken as 2" (2* 1" flange thickness) then the factor comes out to over 3.0 (my ca1 = 13.5"). This seemed straightforward in the initial calculation where only flange areas were considered. But now I wonder, could I consider each flange area separate, thus having 2 distinct breakout areas each with ha = 1"? This would increase the factor further.
With the area of the webs also considered, I increased ha to 8 since that is the total plank thickness and as a result the modification factor is reduced significantly. So in each calculation, the capacity comes out to be roughly the same. Intuitively, that is not realistic because I've only added to the breakout area while holding all else the same.
I searched ACI-318, the PCI Handbook, Manual for the design of Hollowcore Slabs, and various only resources for more information or testing on shear breakout in hollowcore planks but cannot find any information on how to approach this.
To check the plank's capacity, I used ACE318-11 Appendix D ( Section 17.5 in ACI318-14) as advised in the PCI Handbook. Initially, I only considered the breakout area of the flanges for simplicity. The cores will be grouted at the anchors but since the plank has already been cast, the only thing holding the grouted core in place if there is a failure is friction so I cannot account for that to add to the breakout capacity. This calculation does not produce the required strength, so I included the webs of the plank within the breakout area.
This is where things become unclear. The basic concrete breakout strength in shear of a single anchor, Vb, (section D6.2.2 in ACI318-11) needs the required load bearing length of the anchor, le. So question #1: If each flange is 1" thick, the load bearing length, le, is 2" regardless of if the cell is grouted correct? Since the grouted section is not load bearing.
The bigger point of uncertainty is the "modification factor for anchors located in a concrete member where ha < 1.5*ca1" (section D.6.2.8 in ACI318-11). If ha is taken as 2" (2* 1" flange thickness) then the factor comes out to over 3.0 (my ca1 = 13.5"). This seemed straightforward in the initial calculation where only flange areas were considered. But now I wonder, could I consider each flange area separate, thus having 2 distinct breakout areas each with ha = 1"? This would increase the factor further.
With the area of the webs also considered, I increased ha to 8 since that is the total plank thickness and as a result the modification factor is reduced significantly. So in each calculation, the capacity comes out to be roughly the same. Intuitively, that is not realistic because I've only added to the breakout area while holding all else the same.
I searched ACI-318, the PCI Handbook, Manual for the design of Hollowcore Slabs, and various only resources for more information or testing on shear breakout in hollowcore planks but cannot find any information on how to approach this.