nfpa 13 r 2013 edition
more argue:
6.4.6.3.1* Except as otherwise permitted in 6.4.6.3, residential sprinklers shall provide complete coverage of the floor area within the compartments requiring sprinkler protection.
A.6.4.6.3.1 Modern multiple-family building floor plans incorporate certain architectural characteristics or features that can initially seem to make absolute coverage of every single square foot of floor area a challenge. These features include angled walls, wing walls, slightly indented walls, and various soffit configurations.
The “problem” arises when one erroneously considers water discharging from a residential sprinkler to travel only in an absolute straight line, as if it were beams of light. When this approach is taken, small [1 ft2 to 3 ft2 (0.09 m2 to 0.28 m2)] typically triangular “shadowed areas” can in theory be formed on the floor adjacent to their referenced architectural features. The shadowed areas are purely on paper and do not take into account the dynamic variables affecting sprinkler discharge and distribution. It is hardly conceivable that anything located within one of these areas could remain dry during adjacent sprinkler discharge. The committee recognizes that such small theoretically shadowed floor areas are not an issue. Residential sprinkler distribution patterns are specifically intended to provide superior wall-wetting capability. Survivability of the occupants is more dependent on such wall-wetting than on absolute floor coverage.
Though not specifically referenced as such, in fact, NFPA 13 already permits an appreciable amount of “shadowing” by way of the basic obstruction figures and tables for various sprinkler applications. Take, for example, Figure 8.10.6.2.1.3 of NFPA 13, Minimum Distance from Obstruction (residential upright and pendent spray sprinklers). Consider a residential sprinkler spaced 10 ft (3.05 m) off of wall. A 12 in. (305 mm) round column located in the direction of the wall and 4 ft (1.22 m) away from the sprinkler would create an allowable “shadowed” area of approximately 8.6 ft2 (0.8 m2), using the line-of-sight approach.
The intent of NFPA 13R is to provide economically viable, flashover-preventing, survivability-enhancing residential sprinkler layouts. It is not the intent of NFPA 13R to require additional sprinklers for these 1 ft2 to 3 ft2 (0.09 m2 to 0.28 m2) areas.