You did not originally note the sizes, materials, nor pressures etc. of the mains involved, but nevertheless you got some information in many responses. In any case, while I think this kind of issue may be kind of difficult to handle with absolute "standard" verbiage I’ll add just a little more information. One reason is I believe many experienced Engineers (including those pretty good and dedicated ones who assist drafting minimum consensus etc. standards!) understand that occasionally, due to right-of-way restrictions, common utilidors, other strong desires/necessity of the Owner etc., some pipelines inevitably will be placed rather closely together at some point.
That being said, I am aware e.g. I think fairly well-vetted ANSI/AWWA C600-05, Installation of Ductile- Iron Water Mains and Their Appurtenances does contain the words,
“4.3.1.3 Clearance. When crossing existing pipelines or other structures,
alignment and grade shall be adjusted as necessary, in accordance with the contract
documents, to provide clearance as required by federal, state, or provincial, and local
regulations or as deemed necessary to prevent future damage or contamination of
either structure.” and also in another area,
“ 4.3.2.5 Rock conditions. When excavation of rock is necessary, all rock shall
be removed to provide a clearance below and on each side of all pipe, valves, and
fittings of at least 6 in. (150 mm) for nominal pipe sizes 24 in. (610 mm) or smaller
and 9 in. (230 mm) for nominal pipe sizes 30 in. (762 mm) and larger. When
excavation is completed, a layer of appropriate backfill material (see Sec. 4.2.5) shall
be placed on the bottom of the trench to the appropriate depths, then leveled and
tamped.
4.3.2.5.1 These clearances and bedding procedures shall also be observed for
pieces of concrete or masonry and other debris or subterranean structures, such as
masonry walls, piers, or foundations that may be encountered during excavation.
4.3.2.5.2 This installation procedure shall be followed when gravel formations
containing loose cobbles or boulders greater than approximately 8 in. (200 mm) in
diameter are encountered.
4.3.2.5.3 In all cases, the specified clearances shall be maintained between the
bottom of all pipe and appurtenances and any part, projection, or point of rock,
boulder, or stone of sufficient size and placement that could cause a fulcrum point or
pointload.” (See the underlining I’ve added – whether it was originally intended by the standard developers or not someone could certainly argue that other adjacent or underlying pipelines would be at the very least a sort of “subterranean structure” that mustbe considered!)
Now, I think many also well-meaning authorities and individual Engineers have gone far beyond such absolute minimum standards requirements, looking at many additional issues e.g. some as already discussed on this thread (and others regarding potential vulnerabilities e.g. as talked about in some published papers like
). Large diameter and high pressure pipelines obviously might arguably deserve more attention and respect in this regard and many others. It should be remembered as well that at every change in direction or othr thrust foci of more than one parallel pipelines close together, there will in essence be an accumulation of two thrusts for the essentially one soil mass to deal with, and this should probably be appropriately considered in the thrust restraint design..