I'm looking through the classic book "Protective Relaying and Theory and Applications" (attached article). The attached chart is from that book. It says to set the required overload for 90% of the full load amps for a motor with a service factor of 1.0.?? This appears to me to violate the National Electric Code section 430-32 that requires it to be set at 115% FLA...
Can someone explain this?