Scotty said:
Register to use CAT's SpecSizer tool.
.......
Results are generally a little conservative.
Many years ago I was selecting and installing residential standby sets.I did about 8 sets in a short period of time.
All of the sites had multiple air conditioners. All of the installations worked well and all of the customers were happy.
Some years later the first version of Specsizer became available.
I ran the parameters of the existing installations through Specsizer and ALL FAILED.
Why?
Specsizer is excellent software. Why is it failing successful installations.
I believe that it has to do with the default settings.
If you want performance equal to grid performance, use the default settings.
Most applications and most customers will accept a greater voltage dip on a generator than when on the grid.
One of the reasons for the conservative results returned by Specsizer may be the default setting for allowable voltage dip.
Try increasing the setting for allowable voltage drop in Specsizer. It may save you several thousands of dollars on the price of the set.
I would do an RMS loading analysis of the load profile. If the RMS loading is much less than the peak loading then you may consider using a standby rated set.
Will the generator be used for standby service or will the generator be the prime source of power?
If the generator is to be the main source of power, how long will it be in service?
If the installation calls for permanent generator power, a prime power rated set would normally be selected.
However it appears that your load will be highly variable.
As a consultant, at this point I would be asking my customer;
"Why do you want a generator?"
Decorative fountains are not normally supplied with back-up power.
If a generator is being considered because of the high cost of installing grid power, A generator often costs more.
I worked in an area where grid power was diesel generated and was very expensive.
Many homes had standby generators. The cost of grid power was about twice the cost of fuel to run a standby set.
But fuel cost is not the only cost of running a generator. There is the cost of oil changes and repairs. There is the cost of overhauls and/or eventual replacement of the gen-set. There is the consideration of a possible lengthy power outage in the event of a gen-set failure.
All things considered no-one ever considered running their sets full time despite the up-front apparent advantage of 50% cost of running.
How much will it cost to run a generator?
The cost per hour may be estimated:
You can expect to generate 13 kWHrs per US gallon of diesel fuel. Double this figure to get an idea of the hidden costs.
Oh, by the way, that is for a loaded set. The fuel consumption per kWHr increases for a lightly loaded set.
Bill
--------------------