Following up thread238-177655, in the 2008 NEC, this sentence has been added to 240.86(A) regarding series rated OCPD's:
"For calculated applications, the engineer shall ensure that the downstream circuit breaker(s) that are part of the series combination remain passive during the interruption period of the line side fully rated, current limiting device."
Seems overly conservative. If the upstream device, ie high speed fuse, caps current at a level below the kAIC of the downstream device, what does it matter if the downstream device then begins to open during the "downhill" portion of fault current extinguishment? How could the downstream OCPD's opening only diminish the fault level further? (My understanding of a high-speed fuse is it finishes it pre-arcing phase very quickly but that the time to full arc extinguishment is relatively much longer.)
A white paper by GE engineers (see ) stated:
"In practical terms, this will require low-voltage power circuit breakers with 30-cycle withstand ratings on the load side of a current-limiting fuse. Many power systems will not meet these prerequisites. It is doubtful that the engineered series combination solution will become very popular."
Curious, does this recent inclusion in NEC 2008 represent a guideline by which most system coordination PE's would have held anyway? Or is it really more of a victory of, say, circuit breaker manufacturers over fuse manufacturers in the lobbying for NEC code changes?
Thanks much for any help.
"For calculated applications, the engineer shall ensure that the downstream circuit breaker(s) that are part of the series combination remain passive during the interruption period of the line side fully rated, current limiting device."
Seems overly conservative. If the upstream device, ie high speed fuse, caps current at a level below the kAIC of the downstream device, what does it matter if the downstream device then begins to open during the "downhill" portion of fault current extinguishment? How could the downstream OCPD's opening only diminish the fault level further? (My understanding of a high-speed fuse is it finishes it pre-arcing phase very quickly but that the time to full arc extinguishment is relatively much longer.)
A white paper by GE engineers (see ) stated:
"In practical terms, this will require low-voltage power circuit breakers with 30-cycle withstand ratings on the load side of a current-limiting fuse. Many power systems will not meet these prerequisites. It is doubtful that the engineered series combination solution will become very popular."
Curious, does this recent inclusion in NEC 2008 represent a guideline by which most system coordination PE's would have held anyway? Or is it really more of a victory of, say, circuit breaker manufacturers over fuse manufacturers in the lobbying for NEC code changes?
Thanks much for any help.