Engineer1916

Electrical
Jan 9, 2020
42
EngTips Friends,
I have a few 35kV collection circuits coming from a PV farm to a substation. A small portion of the collection circuits will be overhead at a canal crossing. I am trying to determine, do I run separate over head ground conductors for the crossings? Or should I use earth as my ground path for the crossings?

The GSU at the substation is solidly grounded so I have high fault current available.

Any recommendation or references would be highly appreciated.
 
Replies continue below

Recommended for you

Even if you run a separate O/H ground wire across the canal, there is no guarantee that
100% of the GF current is taken by the O/H ground wire. There is always a split factor.
For the safe side, I recommend an O/H ground wire.
 
A sky wire to protect your underground circuits from lightning strikes is a good idea.


--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
I agree with the previous comments, but wanted to add that it may be beneficial to request the interconnecting utilities standard. They can provide very specific guidance on the transition connections.
 
Is your collector system 3-wire with no ground? Unless the crossing is so much taller than rest of the line that it has significantly more lightning exposure, I am unclear why the canal would impact having a forth wire.
 
I visualized buried cable with a ground conductor except for the canal crossing.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
It depends.

Where bacon and I live there's absolutely no value in a shield wire for a short bit of overhead line; heck there's 500kv overhead around here with no shields. But there's places where even 13kV distribution has a continuous shield wire. Like I say, "It depends".

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 