jimgineer
Electrical
- Jun 3, 2008
- 80
A little while back I was trading emails with a PE who claimed to have come up with a way to effectively transmit data over 60Hz (or whatever frequency for that matter) power lines. I have kind of lost touch since then but wanted to get some feedback on thoughts as to whether or not this would be feasible and what kind of regulations or restrictions might be placed on doing so.
One of the big things I'm wondering about is power quality - how much 'divergence' (THD?) from a pure sine wave is one allotted and what standards and terms should I become familiar with to quantify this? Additionally, what is the relationship between THD on for example, the low side of a utility transformer (where control signals might be useful), and the high side of that transformer? Would the reatance of the transformer act to filter out fast rise times on the secondary? I'm picturing putting a square wave directly into the low side of a transformer (no 60Hz signal), would the high side of the transformer essentially be the signal having passed through a bandpass filter?
Additionally, I have run into applications where engineers decide that they need to run control signal wires separate from power wires, and it sounds like the major driving factor behind this is due to electromagnetic interference that is introduced in the signal cables when in close proximity to the power cables. Are there any additional restrictions or codes that govern this or is it simply good engineering practice, depending on the case..?
One of the big things I'm wondering about is power quality - how much 'divergence' (THD?) from a pure sine wave is one allotted and what standards and terms should I become familiar with to quantify this? Additionally, what is the relationship between THD on for example, the low side of a utility transformer (where control signals might be useful), and the high side of that transformer? Would the reatance of the transformer act to filter out fast rise times on the secondary? I'm picturing putting a square wave directly into the low side of a transformer (no 60Hz signal), would the high side of the transformer essentially be the signal having passed through a bandpass filter?
Additionally, I have run into applications where engineers decide that they need to run control signal wires separate from power wires, and it sounds like the major driving factor behind this is due to electromagnetic interference that is introduced in the signal cables when in close proximity to the power cables. Are there any additional restrictions or codes that govern this or is it simply good engineering practice, depending on the case..?