- 12,915
A question for the small generator gurus.
We have a little 290kVA set driven by a steam turbine. Machine was built by Electric Construction in England many years ago, but they have long since passed in to history, and I have no data at all, not even a nameplate.
The machine had a fault before I arrived at site and the exciter was rebuilt. The rotating rectifier diodes were also replaced. I've done all the cold and live commissioning tests I can reasonably do at present - IR's, winding resistances, open circuit curve, voltage balance, exciter diode drops, etc, etc, and all looks reasonably normal. Rated voltage no-load excitation is about 26V and 0.85A.
It stubbornly refuses to self-excite from the residual magnetism in the rotor. The AVR appears to be good - it's an "Anciac 80" by the same manufacturer as the machine - but it isn't giving enough output to build output voltage. If I drive the field externally the AVR tries to regulate once there's a bit more voltage to power it. I am deeply suspicious that the rebuilt exciter parameters are different to the original - fewer turns, different conductor size - but am unable to prove it conclusively. I am getting about 6.4V AC 50Hz between lines on the main output and this is fed back into the AVR. I get about 450mV DC of the correct polarity out of the AVR, but I am not at all convinced that there is enough output voltage from the exciter armature to forward bias the diodes of the shaft-mounted rectifier, which is why it does not build up voltage correctly.
Any thoughts would be appreciated (other than scrap it - that's already on my list
). I wish I was working on a big turbo machine, I know how they work! ![[smile] [smile] [smile]](/data/assets/smilies/smile.gif)
----------------------------------
If we learn from our mistakes I'm getting a great education!
We have a little 290kVA set driven by a steam turbine. Machine was built by Electric Construction in England many years ago, but they have long since passed in to history, and I have no data at all, not even a nameplate.
The machine had a fault before I arrived at site and the exciter was rebuilt. The rotating rectifier diodes were also replaced. I've done all the cold and live commissioning tests I can reasonably do at present - IR's, winding resistances, open circuit curve, voltage balance, exciter diode drops, etc, etc, and all looks reasonably normal. Rated voltage no-load excitation is about 26V and 0.85A.
It stubbornly refuses to self-excite from the residual magnetism in the rotor. The AVR appears to be good - it's an "Anciac 80" by the same manufacturer as the machine - but it isn't giving enough output to build output voltage. If I drive the field externally the AVR tries to regulate once there's a bit more voltage to power it. I am deeply suspicious that the rebuilt exciter parameters are different to the original - fewer turns, different conductor size - but am unable to prove it conclusively. I am getting about 6.4V AC 50Hz between lines on the main output and this is fed back into the AVR. I get about 450mV DC of the correct polarity out of the AVR, but I am not at all convinced that there is enough output voltage from the exciter armature to forward bias the diodes of the shaft-mounted rectifier, which is why it does not build up voltage correctly.
Any thoughts would be appreciated (other than scrap it - that's already on my list
![[wink] [wink] [wink]](/data/assets/smilies/wink.gif)
![[smile] [smile] [smile]](/data/assets/smilies/smile.gif)
----------------------------------
If we learn from our mistakes I'm getting a great education!