QUESTION 1: How to you select SF6 or VCB for different applications.
ANSWER 1: In General, the selection of vacuum or SF6 interrupting devices is dictated based on the following factors: Pricing, individual preferences, national traditions and switching requirements.
Typical application of vacuum and SF6 circuit breakers are as follow:
STANDARD APPLICATIONS:
-a) Motor starter and circuit breaker starter.
-b) Transformer with lactch contactor or circuit breaker.
-c) CircuIt breaker for furnace.
NOTE: Overvoltage assessment it is recommended to determine the requirement of surge protection (arrester and/or surge capacitor) especially if vacuum device is selected for starting large motors and dry type transformers.
ESPECIAL APPLICATIONS:
- a) Back-to-Back Capacitor Bank with reactors: SF6 breaker or Vacuum breaker with synchronous control.
- b) For low frequency application such as railway systems, vacuum breaker is better choice than SF6.
- c) Shunt Reactor application the target maximum overvoltage is limited to 2.5 pu.
QUESTION 2: What is the technical comparison between the two?
ANSWER 2:
Vacuum or SF6 interrupting devices technologies have similar electrical and mechanical performances on standard circuit applications.
Production of overvoltage is the most remarkable difference in performance between vacuum and SF6 interrupting technology. Vacuum devices have tendency to produce significant level of chopping waves and multiple reignitions that could be amplified by the distribution system forcing to exceed the insulation of rotating machines, dry-type transformers and reactors.
QUESTION 3: Why usage of vacuum contactors for lower currents are still not widely used for MV systems?
ANSWER 3:
The smaller standard MV vacuum contactor is rated for 400A(360A enclosed) for a range of voltage between 2200 to 7200 Volts. The require investment associate with starter, MCC, etc. became difficult to justify for small motor capacity.
On the other hand, for large motors the largest standard contactor in the voltage range described above is 720 A (enclosed). The use of the circuit breaker is justifiable since provides larger continuous rating (1200 A minimum), more operation flexibility and better protection features.