what is basic rule for selecting lighting arrester for 13.8KV four wire system.

Is there simple formula?


Thanks in advance for reply.
 
Replies continue below

Recommended for you

If ALWAYS solidly grounded, select MCOV to be about 110 to 120% of the maximum expected operating phase-to-ground voltage. If resistance-grounded or ungrounded, select MCOV to be about 110 to 120% of phase-to-phase voltage.

Assume you meant LIGHTNING arrester. This term is itself obsolete (at least in US) and should now be called SURGE arrester.