SEL-351S Fault Locator Testing

Status
Not open for further replies.

Feedhunter

Electrical
Nov 8, 2010
1
Has anyone come up with a solid method of proving the fault locator algorithm in the SEL-351. I am thinking it should follow similar testing procedures as for distance relays but I am lost as to the equation I would used to get the actual distance and compare it to the relay's result in the SER.
 
Replies continue below

Recommended for you

First off, the algorithm assumes a homogeneous line. If you don't have a homogeneous line you'll never get as good of results as you would otherwise.

After that, SEL has published a great deal of material on the fault location algorithms they use. Contact your local SEL field application engineer for further information.
 