haynewp,
One of the most ignored issues in structural design is in areas where wind loads tend to "control" the design over seismic.
The correct procedure is to develop the loads for both wind and seismic and then design your structural elements for the controlling factor. Too often, engineers determine that the wind is just a little larger, overall, than the seismic, and then proceed to design the entire structure for wind only, ignoring the seismic issues that still actually apply.
For example, while an overall wind load may control the design of a lateral deck diaphragm and brace design, the code requires, in the case of the sligtly lower seismic loads, to factor up the seismic in connection design to ensure that the member fails before the brace. Thus, a steel chevron brace may be based on a controlling seismic load, and its connections as well, while the floor or roof diaphragm may actually be controlled by wind.
It is incorrect to just discard seismic just because the overall primary seismic force applied to the structure is less than the wind load. Both wind and seismic loads must be carried through the entire design, all the way to the foundation, checking each to see which controls in each "piece" of the structure.