I am designing a multi-story warehouse with multiple levels of loading docks. Semi trucks will drive up ramps onto the loading docks and load/unload into the warehouse.
The dead load of the ware house is 75 psf, Live load (Storage) is 300 psf.
We are designing the warehouse using a seismic weight which includes 25% of the storage load per ASCE 7-10:12.7.2
The dead load of the loading docks is 160 psf, live load (Semi trucks) is 250 psf.
For the seismic weight of the loading docks, would you include weight from the semi-trucks? ASCE7-10:12.7.2 allows for public garages and open parking structures to not be included, but this is a little different of a scenario. Also, the code only prescribes minimum loads, and engineering judgement should be applied.
My inclination is to include 25% of the semi truck live loads in the seismic weight.
The dead load of the ware house is 75 psf, Live load (Storage) is 300 psf.
We are designing the warehouse using a seismic weight which includes 25% of the storage load per ASCE 7-10:12.7.2
The dead load of the loading docks is 160 psf, live load (Semi trucks) is 250 psf.
For the seismic weight of the loading docks, would you include weight from the semi-trucks? ASCE7-10:12.7.2 allows for public garages and open parking structures to not be included, but this is a little different of a scenario. Also, the code only prescribes minimum loads, and engineering judgement should be applied.