Seismic tie beam minimum-ACI
ramihabchi
98
is there in aci any requirement about minimum longitudinal reinforcement in seismic tie beams?in ACI 318-11 21.12.3 provisions are given for dimension and tranversal reinforecement.I can t find those related to longitudinal reinforcement and I want to be sure that there is no such requirement in aci.
In general, ACI is more concerned with detailing than strength for design in high seismic activity regions. I don't recall there is such requirement, unless things have changed.
Personally, I would first determine the longitudinal reinforcement required based on the dictated axial load.
Then I might compare that with a "column" 1% limit for axial members found in chapter 10....possibly applying the "architectural column" 50% rule where you can assume a smaller concrete section if the concrete is much larger than that needed by analysis.
Thx
@ JAE what about direct tension? Is there any minimum of longitudinal bars?Is there any provision in ACI about direct tension design as that for axial compression?
I’m not aware of any min reinforcement for tension members- but pile/column Link’s can be either tension or compression.
