LicensedToPEe
thread184-335672
I wanted to get back to this old thread now that it is 2016, 3 yrs after NFPA 13 (2013 print) has been out.
I'm a licensed structural engineer (SE) working with a fire protection engineer (PE) in a project located in TX (that's actually irrelevant) in Seismic Design Category (SDC) "B". What is the current interpretation of the requirements of seismic sway bracing and branch line restraints for sprinkler systems? Please consider the following points:
1.) ASCE 7-10 designates sprinklers as life-safety purpose after earthquake in Sect. 13.1.3 and therefore it does NOT fall under Exemptions per ASCE 7-10 13.1.4, "Item 4. Mechanical & Electrical components in Seismic Design Category B" is not applicable for sprinklers since Section 13.6.8.2 of ASCE 7-10 references NFPA 13 as deemed to meet the requirements of force & displacements of ASCE 7. So far so good!
2.) NFPA 13 (2013) does not make any distinction whatsoever about seismic design categories (SDC). NFPA 13 Section 9.3.1.1 states "Where water-based fire protection systems are required to be protected against damage from earthquakes,the requirements of Section 9.3 shall apply. Who sets this requirement? IBC 2012 does not, it creates a circular reference back to ASCE 7 which goes to NFPA 13.
3.) NFPA 13 (2013) is a Standard, not a legal document (Code). International Building Code (IBC), i.e., the 'Code' with pertaining legal requirements, in Section 903.3.1.1 states: "Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13." There is no other mention of seismic bracing for sprinklers in IBC 2012. Further, 1613.1 Scope "Every structure, and portion thereof, including nonstructural components that are permanently attached to structures and their supports and attachments, shall be designed and constructed to resist the effects of earthquake motions in accordance with ASCE 7". Again, no specific requirements for sway braces and/or branch line restraints for any SDC.
4.) NFPA 13 (2013) Section 9.3.5.9 provides a conservative yet simplified approach to calculate the horizontal seismic loads for the braces. It is using a Cp factor which in turn is tied into the short period response parameter Ss. It lists values of Cp for areas with Ss less than 0.33 with Cp = 0.35 (i.e., 35% of water filled pipe weight is the horizontal seismic force). This would imply that any area of the US, irrespective of the SDC (A or B and higher) would require seismic bracing for sprinklers since there are no areas where Ss=0 on the USGS maps. In other words, even SDC A and B would need to be designed for a minimum of Fp = Cp*Ww where Cp = 0.35.