UcfSE
- Dec 27, 2002
- 2,525
Occupancy category IV, Ss=0.89, S1=0.31, 2006 IBC, ACI 318-05, PCI DHB 6e, V=145mph, Puerto Rico, f'c= 5 ksi, 8" cip walls
I'm having some trouble meeting the ductility requirement at an edge condition for embed plates in a concrete wall supporting steel gravity beams. In a field condition, no problem. Even using the 2.5 times the load exception, a few connections are still giving me problems while others are then ok. I'm checking both the ACI appendix D method and the PCI method (fun).
I'm thinking instead to use tail bars, as shown in an example in the PCI DHB 6e page 6-21. My question is in doing so, since the bars are supporting the reaction in tension, would you consider this to be a ductile failure mode so that I don't need to design the bars for 2.5 times the beam reaction? How do others usually handle the ductility requirement vs the increased load?