- Mar 5, 2011
- 14
Hi everybody,
I have this query regarding Sensitive Earth fault protection. Normally in our installation, the feeder protection for 13.8 kv (distribution) is O/C , E/f ( 50/51,50N,51 N) provided in one relay and Sensitive earth fault (51G) provided in another relay. Presently my contractor has come up with an installation where it is suggested to combine all these functions into one relay i.e. ABB REF 615. My concern is as follows:
My phase CT is 600:1 and cable CT (for SEF is 50:1). Also the relay REF 615 has only one neutral coil for neutral current input. What is the implication of using the cable CT ( 50:1) for E/f protection of a distribution feeder ? Should I insist on separate relays to be provided for SEF and 50/51/51N/50N? I think the earth fault setting will be too low if I use the 50:1 Ct for 51N and 50N protection. Kindly advise.
I have this query regarding Sensitive Earth fault protection. Normally in our installation, the feeder protection for 13.8 kv (distribution) is O/C , E/f ( 50/51,50N,51 N) provided in one relay and Sensitive earth fault (51G) provided in another relay. Presently my contractor has come up with an installation where it is suggested to combine all these functions into one relay i.e. ABB REF 615. My concern is as follows:
My phase CT is 600:1 and cable CT (for SEF is 50:1). Also the relay REF 615 has only one neutral coil for neutral current input. What is the implication of using the cable CT ( 50:1) for E/f protection of a distribution feeder ? Should I insist on separate relays to be provided for SEF and 50/51/51N/50N? I think the earth fault setting will be too low if I use the 50:1 Ct for 51N and 50N protection. Kindly advise.