Gepman, I am using HAP. The equipment manufacture’s electronic catalog allows me to calculate an actual EER value for “proposed building” but as per table 6.8.1A units less than 65K shall be 12.00 SEER as tested to ARI 210/240. Upon reviewing the ARI standard, SEER is then calculated by three tests:
"B" test - cooling steady state - this is run at 80 db 67 wb and 82 db condenser air.
"C" test - steady state dry coil test - this is run at 80 db 57 wb and 82 db condenser air.
"D" test - Cycling dry coil test - this is run at 80 db 57 wb and 82 db condenser air - unit is cycled off and the degradation in cooling energy is measured.
SEER is then calculated as: SEER = PLF(0.5) * EER "B" test
PLF(0.5) = 1 - 0.5 * CD CD is derived from the "C" and "D" tests.
The default is a CD of 0.25
This results in an EER of 13.71 on a SEER 12. This seems wrong due to the EER exceeds the SEER
I find it very odd that we use EER at 95 degrees on larger unit and 82 degrees on small unit in the same model.