Have your motor failures come down after doing this type of test and this type of sealed rewinds?
We have not data. This is the first one we've done. Another one coming in March/April.
Have you tried other of forms mitigation like providing a hood just for the motors to protect them from elements ?
Haha. I'm laughing because I feel I need to tell a long story to answer that.
There are 2 families of outdoor motors.
One family is six 4kv motors which have never had problems where we saw evidence of any water getting in, but yet have had 6 or 7 winding failures among 6 motors in the 22 year life of the plant.
The other family is the one in this thread .. eight 13.2 kv motors which have had a lot of problems with water getting in. We have had 8 or 9 winding failures among 8 motors in the 22 year life of the plant.
In contrast, our other motor families indoor (all have 0 or 1 failure in the same time period among families of 6 or 8).
As for the motor where we have seen water getting in, as stated above "we do everything possible to exclude water". Trying and succeeding are not always the same thing. We have identified numerous points of entry and corrected each one as we identified it. But the paths are subtle. The most recent one is described in
thread237-241996
The point of water entry in that case is leakage across the rusty flange (you can see the rust on the flange surfaces on slides 2 and 9 of attachment to first post in that thread). This is assisted by the vacuum in that area created by the rotor fan action.
I'd say the motor design is somewhat cheap/primitive has some built-in vulnerabilities to begin with. For one, we have huge removable airboxes on top that form part of the inlet air re-direction and filtering. The seal between the airbox and the motor is complex and not easy to access and a challenge to maintain. There have been a variety of improvements and lessons learned along the way, but the paths we discovered were subtle, not obvious, and I don't think we will ever achieve perfection.
The idea of building a hood is more challenging than you'd think. The motor stands high above a CW pit with nothing to brace off of. If you ran long braces from the side of the pit, you would restrict crane access to surrounding equipment. If you mounted the roof to the motor you'd have to mount it to the motor which could increase the weight and change the resonant frequency, and would also limit access required to the top of the motor... including crane on occasion. None of these are insurmountable, but it's a challenge and instead we focus on addressing the local vulnerabilities we identified on by one.
We don't give up on trying to stop the water, but if we can also provide a winding which "doesn't care" if it gets a little wet, that provides "defense in depth" (multiple barriers against failure). The cost to invoke this requirement is about 5% of the cost of a rewind. That is not just cost for the test itself but cost for the rewinder to assume the liability to rewind if it fails during test, which means he does pay much more attention to the endwinding connections of a motor that will be wet-tested. If we made the same investment 10 times and prevented a failure even once, I'd say it was a good investment (considering all the costs associated with failure, which are not limited to cost of rewind).
=====================================
(2B)+(2B)' ?