KenRad,
Independent circuits was the key you mentioned. There is a difference between multiple compressors and independent circuits. You are correct that Trane does not offer that in the sizes mentioned, and I didn't check York.
As far as outside air economizers - you are also correct that SEER/EER can't be better. I stated that. "On paper, the savings from outside air economizers are hard to ignore ..."
Yet, there are significant disadvantages, so much so that in our area of the country, water-side economizers are always preferred. Granted, you are assuming a water-cooled chilled water scenario, and that means a much larger system size than our discussion.
Nevertheless, my preference is still NO air-side economizer, even if that is not the case:
1. Filtration becomes more significant as outside air quantities are increased. Outside air may be polluted, and pollen is also unacceptable. With pollution, the use of air quality or CO2 sensors have become common, in order to limit the amount of outside air in cases where the quality is worse than exists indoors. Additional controls increase cost. Additional filtration increases pressure on the fan - a higher horsepower may be needed, and long-term energy costs increase.
2. Humidification (or the lack of it) is a huge issue. At the very same temperatures appropriate for economizer use, there exist medium or very low humidities. When heated by the load within the space (typically a 3/4 SHR or greater), Relative Humidity levels drop precipitously. These RH levels become a health issue beyond just simple comfort. Anything less than 30% is cause for liability from a health perspective. The humidification systems needed to compensate are more expensive in first cost, and negate much of the operating savings of the economizer.
It should be noted that in many parts of the country, a properly sized, typical SHR-rated unit and heat, with minimum acceptable outside air ventilation, may operate throughout the year with no need for additional humidification. Winter heating may dip below 30% on peak days, but the effect is tolerable for those short periods. Introduce anymore outside air, and that premise becomes moot.
3. Air balance - additional outside air presents a pressurization imbalance in the space. Manually balanced relief dampers do not work in practice - pressures to activate are much greater than typical non-economizer pressurization. Without digressing into a complicated discussion, the fact is that supply distribution occurs at an established pressure (determined with T&B). Yet, the switch between outside air intake with relief vs. return air presents pressure differences that must be absorbed by the fan on the return side. This must happen with no change in pressures at the supply side - or the T&B is violated. In theory, this is impossible.
In simple cases, this difference may go unnoticed. So, smaller units with built-in economizers often work "OK." On a larger scale, this difference cannot be ignored. In fact, the only way to make it work is to use a separate return fan in conjunction with programmed damper control.
By the time you have arrived at all of these disadvantages, an outside air economizer is no real savings.
Sorry - I mentioned it might be beyond the discussion in this thread.