SCR failures typically come from three main causes:
- too much voltage
- too much current
- too much heat
or any combination of the three.
If your application is a SoftStart.... I would ask,
- are you violating the duty cycle limitations ; i.e starting too often without proper elapsed time between starts ?
- Does the unit have proper cooling ?
Also, allowing the SoftStart to source high current for too long a time will raise the heat, and cause SCR degradation and ultimate failure (elevated heat reduces the reverse blocking capability of the devices and they fail)...
Be sure you are operating the SoftStart within the limits and guidelines of the manufacturer.
If you are, the question the plant power. Is it subjected to transient spikes ? A suitable line analyzer can be used to monitor the input voltage to the SoftStart....
Finaly, a defective motor or an interfmittently defective motor...(i.e., stator winding shorts or grounds) can cause failure....
As to pictures of failed SCR's ... you would need an SEM (Scanning Electron Microscope) to be able to see the necessary detail, and an expert in semiconductor analysis to interpret the photos, to be able to "pin-the-tail-on-the-donkey".