I have read several postings that question the quality of carbon steel pipe today versus that 15 or so years ago. I suspect the only source for carbon pipe material today is from recycled steel from mini mills rather than raw steel from blast furnaces. Recycled steel from mini mills was originally provided for bar, rod and tube but in the late 80's the recycled steel began to be used for steel pipe. I am sure the steel specification stayed the same, but did something change in the integrity of the pipe that we are not aware of. The time frame is consistent with our problems.
Our concern is we seem to be getting carbon steel pipe with more interior and exterior mill scale than 15 years ago. On flushing a new HVAC piping installation we were shocked to capture several pounds of iron oxide from the system.
In a several installations where the piping is 12-15 years old, we are finding the exterior of insulated chilled water piping pitted to the level of multiple leaks occurring. The leaks occur principally in 1-1/4" lines but there is everything from 3/4" to 8" pipe installed in the systems. In searching for an explanation we have honed in on a form of concentration cell corrosion as the possible culprit but we are still not sure. In one specific installation leak incidents are isolated but 16 of these leaks over the last 12 years is unacceptable.
Have any of you experienced similar conditions.
Our concern is we seem to be getting carbon steel pipe with more interior and exterior mill scale than 15 years ago. On flushing a new HVAC piping installation we were shocked to capture several pounds of iron oxide from the system.
In a several installations where the piping is 12-15 years old, we are finding the exterior of insulated chilled water piping pitted to the level of multiple leaks occurring. The leaks occur principally in 1-1/4" lines but there is everything from 3/4" to 8" pipe installed in the systems. In searching for an explanation we have honed in on a form of concentration cell corrosion as the possible culprit but we are still not sure. In one specific installation leak incidents are isolated but 16 of these leaks over the last 12 years is unacceptable.
Have any of you experienced similar conditions.