Visiting the above given threads would have cleared your confusion.
Actually, the equation for conversion of ACFM to SCFM is
ACFM = (SCFM x Pstd x T)/[(P-Psat*RH)x Tstd]
Where, P and T are actual pressure and temperature in psia and Rankine respectively, Psat is the saturation pressure of water vapor at the actual temperature and pressure conditions. Pstd is standard pressure, 14.696psia and Tstd is (460+60)R.
A general standard condition is at 60F temperature, 14.696psia pressure and 0%RH but there are some different values across globe.
When you calculate SCFM these are the things you should consider. However, if you are trying to calculate FAD(free air delivery) then atmospheric pressure comes into picture.