TexasPwrEng
Electrical
- Dec 14, 2010
- 15
I'm having difficulty understanding the theory behind an SCCR rating being applied only to a specific combination of devices. A current limiting fuse for example interrupts the current in 1/4 cycle. So the maximum current seen by any device in series with that fuse should be whatever the value is at 1/4 cycle.
Why then can we only use UL approved combinations? It seems to me that the current limiting fuse will interrupt the current at 1/4 cycle, regardless of what other devices are in series with it. The SCCR rating should be based upon the fastest protective device.
I understand that I am wrong, but I don't understand why I am wrong. Does anyone have any insight?