Same Size Breakers in Seires 1
rgpe
Is there any NEC requirement or guidelines relating to breakers of the same ampacity in series?
This would be a situation where electrical system coordination is not necessary.
For example, a 400A main breaker in a panelboard in series with a 400A branch breaker in the same panelboard. Another example would be a feeder requiring a 400A breaker that feeds a 400A panelboard with a 400A main breaker in the panelboard.
It's not a Code violation and is done all the time.
It's actually pretty common when the panelboard or whatever is some distance from the main switchboard and maybe several floors away.
You could feed an 800A from a 400A so long as the cable is protected.