I agree with David that it is ideal to have the CTs in the zone of protection, and that the Trans-Rupters are protecting the transformer. Normally, this ideal is used to ensure that there are overlapping zones of protection and that the interrupting device is in both zones. In this case, however, there is normally no line protection at the station; the line protection is provided at the source and will extend into the transformer. The only thing gained by the expense of the free-standing CT is a very small decrease in permanent line trips. Without the separate CTs, a fault between the Trans-Rupter and the transformer bushing CTs will result in a line trip, a reclose, then a permanent outage unless the fault is temporary. With the CTs, the fault would result in a line trip, a trip of the Trans-Rupter, and a reclose of the line.
If the fault is temporary, having the separate CTs will result in an unnecessary trip of the Trans-Rupter. If the fault is permanent, not having the CTs will result in an unnecessary permanent trip of the line.