RV fire cases - fire zones

Status
Not open for further replies.

Bill3752

Chemical
Joined
Jan 24, 2008
Messages
138
Location
US
Can anyone direct me to where in API 521 I might find a rule of thumb to use for a fire zone. While I recognize that it mainly up to the facility to determine the correct fire zone areas, I did find in a search where the figure of 2500-5000 sq ft was cited. I also found a citation of a 50 ft circle was used. I can't find anything in 521, but admit it was an old version.
 
I could not find anything in my version of API 521 either. For fire calculations, I use a 2500 sq. foot fire circle. This is based on our clients' standards.
 
Thank you both. Joe, I just realized that I have the 4th edition of 521 (1993 version).
 