Looking at the links, I've done a photo analysis (see photo attached). I guess part of this was covered in the 1st thread.
Nonetheless, a quick photo-forensics analysis of the photos (before and after collapse) shows two number 5-pile-groups. A "5-pile-group" is this case is a group of 5-number piles joined by a pile-cap. The pile cap was instead a horizontal I-beam steel member upon which the bridge deck sat. For ease of reference, the 5-pile-group shall be referred to as a Pile-group.
To note, each pile group was well braced width-wise but not length-wise. Or we could say, length-wise, the deck itself was acting at the bracing as well as being supported. Kind of risky though as there would not be enough robustness which would be a necessity on such a project.
Further examination of the available photos, the pile-cap looked like a 400x300 H-Beam (a close match would be 400x300x124kg/m). The Steel pipe used as piles was close to a 400mm diameter (a close match= CHS400x16).
The bracings looked like Steel Angle sections of 75x6 (say EQA 100x100x15).
The Bridge itself was reported to be 7.3m wide and 36m long.
So, when you look closely in the photos, the bracings for the pile group closer to the observer is slightly into the water whereas the other one further away is not. This is a clear indication of substructure settlement in that pile group and absence of a bedrock within the vicinity. And take note that any slight settlement is just enough to induce new out-of-plan forces and moments coming from the supported bridge deck and onto that pile group's weaker direction (length-wise) which eventually widens the span and leads to the collapse, just like in the photo.
So the idea was that the Bridge's weaker longitudinal direction (length-wise) had to be kept in position by the bridge-deck itself on assumption that the piling system was itself well anchored deep into the river bed for a good pile-soil stifness effect and cantilever control effect. This wasnt the case, hence a substructural failure. Therefore a deeper awareness of the geotechnical conditions was a necessity (officially) or a better look into the conditions during construction.
What should have been expected!
1) It'd have been safer to carry out geotechnical investigations to be informed of the soil profile to some 10m deep into the riverbed or where bedrock is encountered for piles to be driven into (say 5m) past the river bed surface or an additional say, 1m into bedrock. I photo-estimated a height of about 8m from the riverbed to the deck level. Longitudinal bracing would have been included to reduce on the cantilevel effect.
Or
2). Simply via experience & ingenuity, no geotech results (...must be goodly-good without doubt), in the helical/screw piling process, the torque readings would have been recorded and analysed for soil's cohesive resistance vis-a-vis the depth screwed into the riverbed for good anchorage and the longitudinal cantilever effect reduced by a bracing feature in addition to the existing bridge deck bracing effect.
This would have countered the following:
- Substructural settlement via well anchorage into the ground
- Longitudinal Cantilever effect via a proposed longitudinal bracing system in addition to the bridge-deck.