This is based on an AFSA interpret I remember from long ago. My memory of it may not be correct any longer. But, here goes:
If you are running the piping on the floor, it is being supported by the floor. The unistrut is only a "convenience" to keep the piping in place. The unistrut is doing nothing to support the piping. Therefore, it is not required to be listed.
If you install piping through open web joists, and lay it on the bottom chord of the joists, it is being supported by the bottom chord. You could in theory, use "zip ties" to hold the piping in place for convenience, as it is not a hanger. The piping is being supported by laying on the joist.
When you hang the piping, that is when you need the listed componets; such as swivel ring, AT rod and beam clamps.
Now, I have never been so brave as to try to get by with "zip ties" as that just seems strange, but I have heard rumors of contractors doing it. If you are in a building that is requiring seismic protection, then regardless of the hanger method, you still must provide the appropriate seismic bracing / restraing.
I can understand the rationale for piping on the floor being secured for convenience. After all, what is a hanger for? It is to support the piping in the air. If the piping is laid directly on the floor, then no additional support is required. You are only using the unistrut as convenience to keep it in place during the installation.
Now, supporting the piping down a column to hose drops is a different story, but can be accomplished if sealed by a Structural PE.
What say ye?