THooper
Electrical
- Jul 19, 2001
- 90
Please give your expert opinion on the photos below. This motor failed due to open rotor bars after several years of service in June. The bars on the failure in June were at the end ring connection point and appeared to be from fatigue. The rotor was re-barred by a rotor re-bar facility, after about four months of service it failed again. The rebuild shop is saying failure is due to a locked rotor stalled condition. The overload protection in place that did not shut it down and is working fine. If you compare to easa photo below you can see the windings in the failed motor did not see a lot of high current, in my opinion no signs of an overload before rotor melt down as easa photo shows. I feel that the rotor failed first due to possible casting flaws in re bar or possible resistance of bars not correct from re bar?