Room design method - attic
rmae
39
As a combustible attic space frequently governs the water demand requirements,the cost of water storage and pump capacity can be lessened by having the /architect contractor separate the attic into 30min. rated compartments with self-closing access hatches between compartments which would satisfy the requirements for room design method.
Any thoughts/concerns?
R M Arsenault Engineering Inc.
I have seen these fire partitions in many apartment complex. The main problem is that these hatches are left open so it may be best to eliminate them.
Not a designer or engineer
Does 13 back this design in an attic???
And we are talking commercial not residental ?????
This is an assembly occupancy so commercial. The main criteria for use of the room design method is the requirement to calculate the demand of a room that has a fire separation that is equal to the required water demand duration. An attic is a light hazard combustible concealed space. If the attic was occupied, you could divide into 30min fire separated rooms and use the room design method. So I see no reason why if it is unoccupied you couldn't divide it the same way and use the room design method. NFPA 13 doesn't explicitly define what a 'room' is.