The opening in the roof would increase your Aoi, and could therefore swap the inequality for condition 1 and move you from a partially enclosed building to an enclosed building. Interesting - hadn't thought of that before. It would also shift condition 2 favorably (if at all). That said, I would certainly never consider it in any design.
So while I agree that the roof opening plays into it, having openings or expanding openings in a roof will not - by itself - push from enclosed to partially enclosed. Going back to my original post, though, there could be other ramifications. If it's possible for the wind blowing over the now breached roof to draw a negative pressure within the building (seems reasonable for an otherwise enclosed space), then you could end up with an effective internal pressure coefficient somewhere between -0.18 and -0.55. To find out just what would have to happen (size of opening relative to roof size/internal volume, location of opening, etc.) for that to happen would require a dive into the background research for wind loading. Something I'd love to do, but don't have time right now.