I don't quite understand the first part of your question. As to the transformer:
Assuming that the transformers have equal KVA ratings;
The transformer with the lower impedance will take a greater share of the current when they are connected in parallel.
If the transformers are not in parallel, then the transformer with the lowest impedance will have a greater available short circuit current.
Under normal operating conditions the transformer with the lowest impedance may have less voltage drop under load.
I say "may" because the PU impedance describes the action under short circuit conditions.
The regulation describes the action under normal loading at a specified power factor.
Under short circuit conditions the transformer impedance is the only impedance in the circuit. Under operating conditions the circuit consists of the transformer resistance, the transformer reactance, the load resistance and the load reactance. Transformer regulation (voltage drop under load) considers these factors at a specified load power factor.
Operating issues? If these transformers are feeding three phases of stator current, the motor will act as an induction generator and try to hold the phase voltages equal. The motor will draw more current from the transformer with the lower impedance. This will tend to create a greater voltage drop in that transformer. The amount of current will depend on the transformer impedance, the transformer X:R ratio, the motor impedance and power factor and the load on the motor.
A seat of the pants estimate:
There is 4% difference in the transformer impedances, The difference in regulation may be 4% or less.
A rule of thumb states that the current unbalance is the square of the voltage unbalance.
With a 4% difference in impedance there may be a 16% greater current in the phase fed from the lower impedance transformer.
Seat of the pants, 10% to 15% greater current in the transformer with the lower impedance.
This is based on the transformers full load current equal to the motor full load current. If the transformers are oversized or the motor is running at less than full load the current estimate will be proportionately less.
If the transformer secondaries are connected in delta a voltage unbalance will create a circulating current which will tend to balance the voltages and reduce the voltage and current differences at the motor.