If I gather this right, on top of the fabric you will only use 2" of Class 5 and in another area 5". I envision the use of fabric normally is to have it at the bottom of a thick layer of aggregation. The purpose is to reduce the thickness of gravel that otherwise would be needed to pas over the weak subgrade. This is sort of like say you have a muddy area in your yard path to the garden and you then spread enough gravel to spread out your foot print so it doesn't sink in in a small area, but instead a larger fear, going in less, due to less shearing of the mud. In your case now suppose instead of that gravel you lay down a sheet of canvas instead of the thicker gravel. You probably won't sink in as far, but still plenty. Add a few inches of gravel on the canvas and it helps, but not much.
So for a very weak subgrade, you might need 18 inches of gravel to drive over it. Instead, you have that fabric at or near the bottom and then carry the same traffic, but maybe with 10 inches.
I liken this to reinforcing concrete to carry a load as a beam. For a reinforced concrete beam the steel is needed near the bottom . Put that steel near the top instead, it then has minimal benefit. So a thin layer of gravel on the fabric is pretty much not going to do noticeable good.
For typical highway use of fabric in the bottom of the base course, and for say a CBR of 3, one may need 18 inches of base, instead of 24" without fabric, depending oon the strength of the fabric. I have seen many a failed use of fabric where the covering with base course is too thin.
For your test, I'd start with 6" at one end of the test and end up with 12 or more at the end, a tapered usage. Fabric on the bottom on the subgrade. Test area length probably 10 feet minimum. In a pinch I'd do the test on one wheel path maybe 4 feet wide.