Reversed Polarity on Closed Delta Bank

Status
Not open for further replies.

bytebyte

Electrical
Sep 25, 2005
32
What effects will reverse polarity have on a closed delta bank? Will the adverse effects on equipment be instantaneous or over a period of time?
 
Replies continue below

Recommended for you

Do you mean reversed phase rotation? If so see itsmoked's answer. Older three phase refrigeration compressors may fail due to lubrication issues. Equipment with phase reversal protection will quietly NOT start.
Do you mean reversed polarity of one transformer in the bank?
Very heavy secondary circulating currents and primary currents. Expect the transformer primary fuses to blow and possibly the distribution feeder to trip out. Possible transformer damage.
Negligible effect on the loads.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 