Return air VFD fan control with return air static pressure

Status
Not open for further replies.

dubbed

Mechanical
Joined
Jul 17, 2006
Messages
37
Location
US
Have a question on how to apply this correctly.
The return fan speed with be controlled with a static pressure transducer in the return duct.

my question is where to put the pressure xducer and is it suction that i need to measure.

This is what I'm using for supply duct pressure after the supply fan
Not sure if this will work for return.
 
ok nevermind. I read the control sequence wrong.
not sure what its goal is.
 
The goal is typically a high limit on suction side (say above 2") to disable the fans before you get a sucked in duct.
 