Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Retaining Wall Minimum Tension Steel

Status
Not open for further replies.

KCPEngr

Structural
Joined
Feb 21, 2012
Messages
4
Location
US
I am designing a cantilever retaining wall using some design software. I am not able to hand calc the same required tension steel as the program. I am trying to use the most conservative requirement from ACI 318 section 10.5 and 14.3. I notice that as I increase the moment on the stem, the As,min requirement increases. Is there a minimum steel calculation that includes the bending stress or moment ratios? Am I not looking in the right place?
 
There is a minimum amount of steel based on geometry and material properties (if loads don't control, obviously), but there is an exception to it based on providing a minimum of 33% higher capacity (I believe- I may be wrong about that number) than analysis shows is required. Don't have ACI in front of me, so I can't point you to the right provision.
 
Look in ACI Section 10.5 - frv is right in that the program is probably using 1.33 x As(req'd) as the minimum amount as long as As(req'd) is less than the other minimums.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top