As per Mechanical Code the for restrooms,the level of exhaust typically is 50 cfm per water closet or 2 cfm per square foot.

What is exhaust (cfm) of wash basin/lavatory?

In case if cooling is required, how to size the supply cfm of the restroom ?

 
Exhaust is still 2 CFM/SQ.Ft.

Supply air CFM = effective room sensible heat/(1.08*dt)
dt = room design temp (Deg.F)-lvg. coil db temp (Deg.F)
sensible heat in BTUH


 
BUT if you calculate you need 200 cfm supply air for whatever reason and you also decide to meet code with 50 cfm exhaust, it's a bad design. These spaces should remain negative to typical surrounding areas...
 
in case if cooling is required in restroom, how to maintaine -ve pressure and suppling cooling at the same time with out effecting the comfort requirment. is there any guides?


regarding the required exhaust cfm for wash basin/lavatory, for the reason of removal of humidity is there any fixed exhaust rate? I think 2 CFM/SQ.Ft.is not enough espically in humid weather.
 
Don't look to perfectly condition a restroom. Or a locker room. Exhaust what is needed to remove odors and steam from showers and make up that volume via transfer grilles connected to a conditioned space.
 