It depends on what you want the relay to do.
If you are looking for a flow of fault current from the CB side into the generator then connect the relay to CT's at the CB end. The thing is, if your generator can run in island mode all by itself an OC relay connected to CT's at the CB end will not be able to detect an internal generator fault as (neglecting contribution from in-service motors) there will be no flow of fault current for the relay to "see".
If you want the OC relay to be able to detect an internal generator fault and there is any chance that the generator can run in island mode all by itself, then connect the OC relay to CT's at the starpoint end. A relay so connected will also detect faults external to the generator.
Also, take care. The OC relay may need to have a voltage dependent characteristic, it depends on what you want it to do.
As to how a modern multi-function relay is configured, I concur with jbartos, it depends on the model and the manufacturer. I have just completed a generator protection relay installation using Alstom P343 relays. These relays utilise phase CT's at both the CB and the starpoint ends, with the CT's at the starpoint end being used for OC protection.
Alstom's less capable generator protection relay, for smaller machines that typically are not fitted with CT's at the starpoint is the P342. This relay has provision for CB end CT's only so (naturally) the OC protection will utilise CT's at the CB end.
So, what is correct? I think definately use CT's at the starpoint end if the generator can ever operate in island mode. You should also have a look through IEEE C37.102, a very useful standard, and have a think about exactly what protection you are trying to provide. Also, many manufacturers have excellent information on their websites and you should check these out.
Regards