As shown, the CT is on the grounding jumper to the right of the neutral terminal. The CT will not see any line to neutral load current. The CT will see line to ground current.
For an example, consider the CT to the left of the terminal. The CT will now see all neutral current, both line to neutral and line to ground.
Now consider a variable load connected line to neutral on one phase. The neutral CT (now placed to the left of the terminal) will see this load current. Now increase the load. The current seen by the CT will increase.
Continue to increase the load until the load current reaches fault level. At no point will the current reverse.
Now reconnect the load from line to ground. Apply and increase the load. The results will be the same, no current reversal.
Now consider a winding fault on an unloaded transformer.
If we consider a fault at the 95% point on one winding, then we may simulate this by connecting our test load from a -5% tap to ground.
Same result. No reversal of current.
I accept that the OP saw a reversal of current.
I believe that the question is:
Why was the test set showing a current in reverse of the normal current before the test started??
Concerning delta connections:
If the transforme under test was feeding a wye:delta transformer with a four wire primary connection, it may be possible for the fault current to reverse.
CT position:
If the CT is to the right of the terminal as shown, the CT will see only ground currents.
If the CT is to the left of the terminal, the CT will see both ground and and line to neutral currents.
Another possible cause is if one of the test connections was inadvertently made to the neutral terminal rather than to the proper ground position. Such a connection may allow the fault current to split and part of the current to return via the grounding jumper (and CT) in the reverse direction.
Bill
--------------------