rockman7892
Electrical
- Apr 7, 2008
- 1,178
I have attached a schematic for a High Resistance Ground (HRG) system that we cannot seem to get working. The system voltage is 480V.
In the schematic I have referenced where the ground is connected to at the bottom and also where the resistance network connects to the transformer nuetral.
There is a pushbutton labeled "TR" that can be used to test the package however when we push this button we see no current flowing through the network nor does the voltage relay HMR pickup. We have traced through the whole system and checked for coninuity and do not see any problems in that regard.
We took voltage readings from PH1-N at "Measuring Point A" that is referenced and got a reading of 280V. However when we press the TR button to test the system this reading drops to 23V and we see no current flowing in the system as stated above. I then removed the ground connection at the bottom of the drawing and connected the #8 wire shown directly to the bottom of the first resistor HREA. Again I had 280V at the measuring point, however when I pressed the TR pushbutton the reading dropped to 0V.
I cannot firgure out what is going on and why this system isnt working. Am I missing something?
I've had the OEM come into look at this and they are puzzled to and are trying to figure it out but I'd figure I'd see what you guys thought in the mean time.