resistance coefficient - T fitting 1

Status
Not open for further replies.

kagadpencil

Mechanical
Jun 15, 2004
38
in a duct system of ours, we had a T fitting to allow for gas flow in perpendicular direction to the main flow direction. Then we decided not to allow that flow and hence we blanked the opening off using a wooden plank. But since it is not 100% air-tight, there is some resistance coeff. associated with this section. Can someone please point me to the correct source to look up to calculate the resistance coefficient for this section. I was looking in ASHRAE 1992, but could not find anything relevant.
 
Replies continue below

Recommended for you

actually, there is no air leakage, but the geometry is causing turbulence in the chimney stack following the T joint. Thus this turbulence is giving rise to additional flow resistance and hence pressure drop -- can some one point me in the right direction to look up some stuff to come up with a flow resistance value for whatever that is going on (turbulence) in that T joint.
 
Many hydraulic handbooks have resistance coefficients.

I believe from your explanation that the flow you now have cotinues straight through the tee and the sideways branch is the one blanked off. The resistance for a tee in that flow configuration has an equivalent pipe length (L/D) of 20. If the flow has to make a 90 degree turn and flow out the branch, the L/D increases to about 60.
 
TD2K (Chemical):

I think your tip is helpful.

I was looking into "Hand book of Hydraulic Resistance" by Idelchik. I have not found any mention of such case there. May be I am not looking carefullly.

Can you please tell me the book source where I can get the info that you provided? I will like to quote that source in my report.

Thank you very much.
 
Also,
When calculating the pressure drop, I understand that I need to take L/D as 20, but what value of f should I use ? --- Is that the same as used for the pipe ? -- The one that was calculated from Moody chart ?
 
A reference of L/D=20 for a straight run can be found in Crane Technical Paper No. 410. This is based on testing of pipe in turbulent flow and may be good for you.

I recommend you consider posting this same question in the Mechanical/HVAC forum. As you are probably dealing with fractional inches of water pressure drop where velocity head is a significant component, there could be additional considerations for your system beyond the general chemical engineering experience with piping systems. Just a thought, SShep
 
Unless the flow or velocity is high, you should be able to ignore the pressure drop. The "K" for a poor bend is around 1.2, for a radius bend is around 0.7 and for a good quality air turn mitre bend would be 0.35, so a minor obstruction would be under 0.30.