A main drain test can also be used to check for obstructions. Example, I watched a main drain go from 80 static to 15 psi residual. Turns out the butterfly valve on the riser that had an indicator noting it was open, was actually about 80 closed. This was discovered when the contractor removed the valve. False sense of security. Same thing can happen on PIV,s and I have seen that as we'll.