Going back to the equivalent circuit, see figure 2b here:
It shows the s dependence shows up simply in R2/s. As s continues to increase beyond 1, current continues to decrease although as you observe relatively slowly because the impedance is primarily inductive as we pass down to zero speed and reverse speed.
For sake of addressing the negative resistance element, I'll mention that we can separate R2/s into two components.,... one that "delivers power" to the shaft (under normal forward rotation) and one that corresponds to rotor losses. This is accomplished by subracting R2 (resistive loss portion) from R2/s, which results in R2/s – R2 = R2*(1-s)/s (this is the component associated with power delivery to the shaft). If we are in steady state with speed between 0 and sync (slip between 1 and 0), then the term is positive corresponding to "motor action" in the sense that real power flows from electrical system to mechanical system. If we go below 0 speed (above slip=1), then you can imagine that to maintain this state of affairs in steady state we have to be applying force to the rotor in direction opposite motor torque. This corresponds to generator action since real power would be flowing from mechanical to electrical system. That is the physical singificance of the he term R2*(1-2)/s becoming negative.
I may be out of line, but it occurs to me it may be productive if the original poster can take a step back and describe what he is seeing from beginning to end.
I gather a motor is spinning backwards and trips during start on instantaneous for MCP breaker?
Trips every time? Trips intermittently? Would you care to share the motor data and the setpoint? Maybe a high-efficiency motor? Have you monitored the current? If so what kind of clamp-on ? How fast is it spinning backwards? How long does it take to start onj a successful start? Ever tripped when not spinning backwards?
Tripping of MCP breakers is a subject near and dear to my heart and I have shared some of my pain and lessons ont eh forums. I agree backward rotation could in theory increase the initial current but it is certainly not the only possible cause of an instantaneous trip.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.